Quote:
Originally Posted by Mikej View Post
I would replace the flexible line with black pipe. Was the entire 75 ft run of corrugated bubble tested? If it was bent too much it could leak.
Guessing that part of the run is in a wet location where black pipe is not going to hold up. I replaced black pipe with flexible stainless on a run through a crawl space where rust had nearly penetrated the black pipe.
Reply With Quote
  #17  
Old 06-12-2019, 08:04 PM
Mikej Mikej is offline
Senior Member
 
Join Date: Nov 2004
Posts: 3,949
Quote:
Originally Posted by oliver1850 View Post
Guessing that part of the run is in a wet location where black pipe is not going to hold up. I replaced black pipe with flexible stainless on a run through a crawl space where rust had nearly penetrated the black pipe.
Interesting I had figured this was in a basement. Still wouldn’t want to bury ss corrugated, but the poly mentioned earlier may be the answer IF it needs to be buried, but again it was mentioned you couldn’t bury ss corrugated.

Last edited by Mikej; 06-12-2019 at 08:08 PM.
Reply With Quote
  #18  
Old 06-12-2019, 08:24 PM
Black Dog's Avatar
Black Dog Black Dog is offline
Riding Along
 
Join Date: Aug 2010
Location: Rockwood ON, Canada
Posts: 6,241
Quote:
Originally Posted by AngryScientist View Post
firts off, if they were just using soapy water, that's not good enough for small leaks, a product called "snoop" is much more sensitive with bubble action to find small leaks because it doesnt run off as fast:



you may pick up a bottle of that and test yourself to prove where the leak is or might be.

realistically though, you paid someone for an installation and now you smell gas. as flash mentioned, the whole reason they oderize gas for residential applications is for safety concerns to alert people of leaks; and if you and others smell gas - there is obviously a leak. i would push the issue until they fix you up - that's part of a complete job.

if they arent too responsive and you want to fiddle with it, i'd shut the gas off, take apart the union to the flex hose, clean the mating surfaces, grease the threads and re-tighten everything - that might just fix your issue without too much hassle.
Greasing threads is not what should be done with gas line connections. Joint compound with teflon is what should be used.
__________________
Cheers...Daryl
Life is too important to be taken seriously
Reply With Quote
  #19  
Old 06-12-2019, 08:31 PM
Hellgate's Avatar
Hellgate Hellgate is offline
Senior Member
 
Join Date: Feb 2018
Posts: 1,819
And I thought you were talking Mexican food...
Reply With Quote
  #20  
Old 06-13-2019, 01:23 AM
oliver1850's Avatar
oliver1850 oliver1850 is offline
Senior Member
 
Join Date: May 2010
Location: northern IL
Posts: 9,213
Quote:
Originally Posted by Mikej View Post
Interesting I had figured this was in a basement. Still wouldn’t want to bury ss corrugated, but the poly mentioned earlier may be the answer IF it needs to be buried, but again it was mentioned you couldn’t bury ss corrugated.
My guess is that the source connection is in the basement but it runs through the foundation and underground to the generator.

For burial it's supposed to be inside watertight conduit. I don't know what other options there are for direct burial, but I'm guessing stainless pipe would be one. On our farms where LP is the gas used, it's common to use copper tubing for direct burial. Don't know if that is recommended for NG.

The most corroded place in the black pipe I removed was actually not in the crawl space, but about 6' inside the basement wall, on the bottom side of the floor joists.

Last edited by oliver1850; 06-13-2019 at 01:26 AM.
Reply With Quote
  #21  
Old 06-13-2019, 07:38 AM
wallymann's Avatar
wallymann wallymann is offline
Senior Member
 
Join Date: Aug 2008
Location: motown, michigan, usa
Posts: 4,993
Quote:
Originally Posted by Mikej View Post
Pretty sure the corrugated flexible line runs through the basement and is connected to the main hard plumbed black pipe to the generator, so it’s not the generator valve to be concerned about, that’s outside. Replace the line with black pipe, I was a pipe fitter at one time.
correct. the CSST installation runs entirely inside the house (2/3 basement and 1/3 crawlspace), except for the connections to the gas-main and to the generator which use short sections of black pipe until inside the rim-joist.

i picked up a couple sniffers. a continuous monitoring deal i can leave in various locations to track over time, as well as a flex-neck deal i can point at connections and such to ID/target leaks very precisely.
__________________
walter | motown, michigan | usa
>>> mijn fietsen <<<

Last edited by wallymann; 06-13-2019 at 07:54 AM.
Reply With Quote
  #22  
Old 06-13-2019, 07:52 AM
AngryScientist's Avatar
AngryScientist AngryScientist is offline
Administrator
 
Join Date: Mar 2010
Location: northeast NJ
Posts: 33,154
Quote:
Originally Posted by Black Dog View Post
Greasing threads is not what should be done with gas line connections. Joint compound with teflon is what should be used.
BlackDog - I agree that pressure retaining threaded connections should use joint compound, but i was talking about the threaded connection on a union that is only used to force the machined mating surfaces of the union itself together. it's helpful to grease those threads to get easier engagement to force the mating surfaces together. Getting them together straight with clean mating surfaces is key, and enough pressure from the threaded connection to keep leaks down.

Reply With Quote
  #23  
Old 06-14-2019, 03:23 PM
Hawker Hawker is offline
Senior Member
 
Join Date: May 2007
Location: Gainesville, GA
Posts: 2,383
Man...I've learned a lot from this thread. When did all you guys get so smart?

Good luck, OP. I suspect that perhaps "teensy gas leak" may be an oxymoron.
Reply With Quote
  #24  
Old 06-14-2019, 09:43 PM
Dekonick's Avatar
Dekonick Dekonick is offline
Senior Member
 
Join Date: Dec 2003
Location: Howierd County, Maryland
Posts: 6,440
Quote:
Originally Posted by Hindmost View Post
I wouldn't be comfortable with this situation either. Under the circumstances I don't think the bubble test (soapy water right?) is sufficient. Did the contractor do a pressure leak down test when installed? Will he do leak down test now?

Also, what can be said about the integrity of the generator?
BINGO -Did they do a pressure leak down test? I'll bet not. IN ADDITION - I would not accept yellow CSST gas line in my home. It is a fire hazard implicated in many lightning strike fires. Lightning strikes, heats the CSST, creates a pin hole, auto ignites the gas, and you have a tiny gas fed flame... wherever that pinhole happens to be. In the crawl space, wall, wherever. They say it can be prevented by proper bonding... I am not convinced. Often the plumber says the electrician should do it... the electrician says it is the plumbers problem... or if it is a project addition later on... who knows? It may be code today, but if I were a betting man, I'll bet sooner or later the code will change. You can get the black CSST - that is a commercial grade. It isn't as good as iron pipe, but better than the yellow crap. JUST MY OPINION but do a little research and you will find out this is all true. All I know is I have seen quite a few homes burn to the ground where the yellow CSST has been implicated... Now - to find a tiny leak: Replace the fittings. If the problem persists, it is probably the CSST. Do check your other gas appliances too...

Best of luck.
Reply With Quote
  #25  
Old 06-14-2019, 09:48 PM
Dekonick's Avatar
Dekonick Dekonick is offline
Senior Member
 
Join Date: Dec 2003
Location: Howierd County, Maryland
Posts: 6,440
Quote:
Originally Posted by oliver1850 View Post
My guess is that the source connection is in the basement but it runs through the foundation and underground to the generator.

For burial it's supposed to be inside watertight conduit. I don't know what other options there are for direct burial, but I'm guessing stainless pipe would be one. On our farms where LP is the gas used, it's common to use copper tubing for direct burial. Don't know if that is recommended for NG.

The most corroded place in the black pipe I removed was actually not in the crawl space, but about 6' inside the basement wall, on the bottom side of the floor joists.
Continuous copper can be buried, at least by code Ellicott City.
Reply With Quote
  #26  
Old 06-14-2019, 10:04 PM
Tandem Rider Tandem Rider is offline
Senior Member
 
Join Date: Jun 2012
Location: Bend OR
Posts: 1,921
Quote:
Originally Posted by Dekonick View Post
Continuous copper can be buried, at least by code Ellicott City.
Copper sometimes reacts with Natural Gas, pinholes and leaks down the road. I can't imagine direct burying uncoated copper for any fuel gas, I've seen too many leaks over the years on refrigerant and water lines.

Finding the leak usually isn't too hard, unhook and cap or plug the line at each appliance and the meter connection. Pressurize with air to 60 to 100 psi, listen for the leak, if you don't hear it, leak soap will find it. Fix the leak(s), double check every single joint, the re-connect each appliance and leak check the new connections with soap.
Reply With Quote
  #27  
Old 06-14-2019, 10:26 PM
Dekonick's Avatar
Dekonick Dekonick is offline
Senior Member
 
Join Date: Dec 2003
Location: Howierd County, Maryland
Posts: 6,440
Quote:
Originally Posted by Jaybee View Post
The "sniffer" is probably a PID, or photoionization detector. Should be able to detect methane down to the single PPM range, and the utility field crews should carry them as a safety tool.
Yes - There are meters, and there are meters... Nothing you buy is going to compare to anything the gas co field units carry. The PID units are expensive...

The black CSST is a far superior product to the yellow. https://www.mopropanesc.org/news-1/arc-resistant-csst

http://www.tracpipe.com/technical/cs...-instructions/

https://www.youtube.com/watch?v=OpGsZ4xxzj8

Video with plumber showing a cut off section of yellow CSST with a pinhole from an arc from a lightning strike https://www.youtube.com/watch?v=BOfioT9fq6Y

Last edited by Dekonick; 06-14-2019 at 10:33 PM.
Reply With Quote
  #28  
Old 06-14-2019, 10:41 PM
Dekonick's Avatar
Dekonick Dekonick is offline
Senior Member
 
Join Date: Dec 2003
Location: Howierd County, Maryland
Posts: 6,440
Quote:
Originally Posted by Tandem Rider View Post
Copper sometimes reacts with Natural Gas, pinholes and leaks down the road. I can't imagine direct burying uncoated copper for any fuel gas, I've seen too many leaks over the years on refrigerant and water lines.

Finding the leak usually isn't too hard, unhook and cap or plug the line at each appliance and the meter connection. Pressurize with air to 60 to 100 psi, listen for the leak, if you don't hear it, leak soap will find it. Fix the leak(s), double check every single joint, the re-connect each appliance and leak check the new connections with soap.
Does anyone still have 'wet' gas? I digress - Personally, I wouldn't use copper but it was code last time I checked. I DEFINITELY would not use non-arc protected CSST. Valid point on copper - just like water lines, copper can corrode. Wet gas, contaminated with other hydrocarbons and sulfur and sometimes water vapor, can be quite harsh on plumbing.
https://www.eia.gov/energyexplained/...tural_gas_home

Last edited by Dekonick; 06-14-2019 at 10:46 PM.
Reply With Quote
  #29  
Old 06-14-2019, 11:00 PM
Black Dog's Avatar
Black Dog Black Dog is offline
Riding Along
 
Join Date: Aug 2010
Location: Rockwood ON, Canada
Posts: 6,241
Quote:
Originally Posted by AngryScientist View Post
BlackDog - I agree that pressure retaining threaded connections should use joint compound, but i was talking about the threaded connection on a union that is only used to force the machined mating surfaces of the union itself together. it's helpful to grease those threads to get easier engagement to force the mating surfaces together. Getting them together straight with clean mating surfaces is key, and enough pressure from the threaded connection to keep leaks down.

Ok. I agree. Grease in that application is fine. Some jurisdictions would still not allow it but not for any safety or functional reason just to reduce risk of using greas on pressured threads. Teflon joint compound would do the same job as grease. But I am not disagreeing with you.
__________________
Cheers...Daryl
Life is too important to be taken seriously
Reply With Quote
  #30  
Old 06-14-2019, 11:07 PM
Dino Suegiù Dino Suegiù is offline
Senior Member
 
Join Date: Sep 2018
Posts: 1,105
Quote:
Originally Posted by Tandem Rider View Post
Copper sometimes reacts with Natural Gas, pinholes and leaks down the road. I can't imagine direct burying uncoated copper for any fuel gas, I've seen too many leaks over the years on refrigerant and water lines.
Yes. What is ironic is that while Natural Gas itself isn't really corrosive to copper pipe (which should be graded for NG and not just water or propane, btw) what usually causes the copper to corrode is the hydrogen sulfide/sulphur which is added to the NG as the warning odorant. So, the corrosion can occur regardless of the copper pipe's location.

There is even a prescribed HS limit per x SCF of copper pipe, so one needs to know the HS content of the locally supplied NG.
Here, but if using copper I would verify if that formula is still current:
"Copper and copper alloy tube (except tin-lined copper tube) should not be used if the gas contains more than an average of 0.3 grains of hydrogen sulfide per 100 standard cubic feet (scf) of gas (0.7 mg/100 L)."

As Mikej and others wrote, Schedule 40 black iron is just safer than copper. If exposed to heavy moisture/underground, then poly. Long runs of corrugated...just add up all the extra surface area prone to kinks and pinholes, so again also best avoided when possible. Copper and CSST flex are the worst options for NG.

Regardless, whatever the material, if I smelled gas in my house, especially to the extent the op has, I would definitely not risk it nor rely on soapy water, other half-means, not even "sniffers" I was operating myself as I'm not a plumber and NG isn't H2O:
I would have a qualified professional source out the issue and properly repair it (and probably avoid copper and/or CSST flex as much as possible, preferably entirely, as dekonick recommended above).
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 12:10 PM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2024, vBulletin Solutions, Inc.