PDA

View Full Version : OT: PVC drain pipe failure above ceiling


dddd
05-30-2020, 12:47 PM
I generally don't post OT's, but plumbing is not my specialty and I am perplexed by the complete failure of a ~25-y-o 1.5" PVC bathroom drain pipe that runs overhead above a downstairs hallway.

Was sitting here at my computer just yesterday, post-ride lunch and catch-up on my Email and forums. Suddenly I started hearing the "tink tink" of water drops landing on some nice alloy rims. I immediately headed downstairs to see a 1 foot diameter bubble of latex paint hanging down from the ceiling surface. I ran outside, shut off the water, grabbed a bucket and got the bucket under the huge, dripping paint bubble.
I poked the bubble with a screwdriver and almost a quart of water rushed out. The dripping ceased completely within minutes.

So I cut out a square of sheet rock to the centerline of the nearest stud, looked up and saw the black sch40 1-1/2" pipe with a slightly irregular crack nearly clean through it.
There was evidence of this leak having been seeping for quite a while, rusted drywall screws and moldy delamination under the cardboard facing.

I ran a saw though the jagged crack line and fitted up a rubber coupler for a convenient fix to the plumbing.

My questions are what caused this failure, and if the rubber coupler is sufficient to hold up to long-term use including chlorinated cleaning and drain-clearing products?
And I'm thinking that perhaps some design rule may have been overlooked having to do with accommodating length-wise thermal expansion. Hoping that the rubber might help here(?).

https://live.staticflickr.com/65535/49952978712_330df7ea79_b.jpg

yarg
05-30-2020, 12:58 PM
Can't imagine why a PVC pipe would crack. Furnco fittings are quite durable as long as you support any pipe load so there isn't any shear at the splice and there isn't a huge gap between the two pipe sections. If no problems there and hose clamps are tight you should be good.

Tony
05-30-2020, 01:02 PM
Not sure what caused the failure, maybe not supported properly in the area of the failure. Also, excessive glue around a joint can also weaken the pipe and cause failure.
I've seen these rubber couplers last over 25 years and not leak. If there was little space between the two pipes after cutting and joining the two with the rubber coupler there should not be a problem of sewage moving freely.
If this was under the house I would not worry. Because its in the ceiling I would replace it properly by cutting out the bad and re-gluing another piece of pipe to this system.

dddd
05-30-2020, 01:11 PM
Not sure what caused the failure, maybe not supported properly in the area of the failure. Also, excessive glue around a joint can also weaken the pipe and cause failure.
I've seen these rubber couplers last over 25 years and not leak. If there was little space between the two pipes after cutting and joining the two with the rubber coupler there should not be a problem of sewage moving freely.
If this was under the house I would not worry. Because its in the ceiling I would replace it properly by cutting out the bad and re-gluing another piece of pipe to this system.

Thanks, Tony. I am recalling that a helpful pro plumber that happened to be in the plumbing aisle at Home Depot seemed to be telling me about all of what you just wrote.
Perhaps I didn't fully appreciate the need for a smooth inner surface and there was/is a missing chunk leaving a 9/16" gap about one third of the way around and to the bottom. He recommended using two shorty rubber couplers with a short length of new pipe between them, ostensibly to facilitate installation and to leave a smooth inner wall.

Oh, and I really lucked out here in that my very last use of the bathroom had been for taking a shower!

Do you think that the ends of the pipe should have some amount of give in the lengthwise direction to-and-fro, to accommodate thermal expansion?
Would solid glued-up attachment sufficiently accommodate expansion if the ends now feel rigidly fixed (without my coupler) where the break is?
I don't know how I would assemble a glued pair of couplings unless I removed the inside mating/centering ridge from at least one of them (since the ends won't flex in the lengthwise direction).

Tandem Rider
05-30-2020, 01:12 PM
The Fernco fitting is fine for long term use, however, you need support under each side of the new splice to keep the shear load off of the rubber. Just nailing a couple of boards between the joists would do it.

weaponsgrade
05-30-2020, 01:17 PM
Some standing water froze?

robt57
05-30-2020, 01:34 PM
Some standing water froze?

Or the original installer didn't see the crack in the new material from pre-install mis-handling tossing etc. Or didn't care because it was Friday...

paredown
05-30-2020, 02:03 PM
I'm seeing black pipe, so ABS, not PVC. Talk to two plumbers, get three opinions, but our master plumber does not like ABS because it is more prone to damage--I would lean towards damage before install.

Fernco is fine and will meet code because it will be covered up.

NHAero
05-30-2020, 02:07 PM
If this were my place, I'd get a short piece of the same 1-1/2" pipe (BTW - you mention the last use was a shower - showers are usually plumbed with 2". And if you meant, not a toilet flush, that pipe is way too small, would need to be 3") and a coupling. Slide the Fernco onto one pipe past the joint, glue in the new piece with the coupling so that there is essentially no gap between the old cut piece and the new piece, then slide the Fernco back over the (no) gap and tighten.

If you want to be extra cautious, make up the new piece with a clean-out in it.

Finally - not a plumber, but in my experience in New England I have never seen black PVC - all black DWV piping is ABS. They are NOT compatible in terms of the glue used.

If I can help further PM me.

dddd
05-30-2020, 03:10 PM
Thanks all, I now realize I was very likely incorrect about how the bathroom is really plumbed.
Now I'm thinking that this pipe must be just for one or both of the bathroom sinks, and that the toilet and tub drain likely straight down the wall of the laundry room directly below.
That would be great, because presumably now I don't have to worry about the inside of the joint being perfectly smooth(?). There was that chip off one of the pipe ends after I ran the saw through the crack.

And robt57 you are probably right about the pipe having got dinged/cracked somewhere along it's journey to it's present location!

I should have mentioned that it actually doesn't get that cold here and that this pipe is central within the house.

I suppose I could slide the coupling away and test-flow which bathroom appliances actually empty into this pipe. Or, wait, I'll just run hot water to do that!

And I will wrap the OD of the coupling with beer can sheet (two layers of a thicker-wall larger beer can) and secure that with a pair of clamps to better preserve the alignment of the two ends.

This is the kind of feedback that I hoped would come from this great forum.

Dino SuegiĆ¹
05-30-2020, 03:48 PM
Thanks all, I now realize I was very likely incorrect about how the bathroom is really plumbed.

Now I'm thinking that this pipe must be just for one or both of the bathroom sinks, and that the toilet and tub drain likely straight down the wall of the laundry room directly below.
This is certainly the case, because a toilet drain line would be 3" diameter minimum by code, 4" diameter common, for obvious reasons.

And robt57 you are probably right about the pipe having got dinged/cracked somewhere along it's journey to it's present location!
This is the most likely explanation.

I suppose I could slide the coupling away and test-flow which bathroom appliances actually empty into this pipe. Or, wait, I'll just run hot water to do that!

And I will wrap the OD of the coupling with beer can sheet (two layers of a thicker-wall larger beer can) and secure that with a pair of clamps to better preserve the alignment of the two ends.
Since the existing pipe is ABS (black; Acylonitrile-Butadiene-Styrene), and although both ABS and PVC (white, Poly-Vinyl Chloride) are allowed by code, the solvents/glues/joining methodologies are different and really should never be mixed, ie never use ABS solvent/glue on PVC and vice versa.

For long-term peace-of-mind repair I would recommend:
2 clean cuts removing some additional minimum length of "OK" pipe on either side of the crack, to be safe
+
a bridge piece of new 1 1/2" SCH40 ABS (Edit: I see NHAero suggests this as well, above)
+
2 new Fernco clamps
+
2 galvanized "U" hangers holding the (extant, not the new middle repair piece) pipe to the plywood substrate above, but still allowing lateral movement of the pipe.

wallymann
05-30-2020, 05:14 PM
Oh, and I really lucked out here in that my very last use of the bathroom had been for taking a shower!

my understanding is that gray water and true sewage must be routed separately...is that not the case?

dddd
05-30-2020, 06:15 PM
my understanding is that gray water and true sewage must be routed separately...is that not the case?

I wanted to know how the two sink's drains were routed in that regard, so I ran water in each one and went downstairs to listen to the pipe.

The two sinks are on separate drain lines, at least at that level of the house. The pipe that broke turns out to serve just the one sink, so it was just a coincidence that it failed completely some minutes after I took my post-ride shower.

dddd
05-30-2020, 06:46 PM
I was putting in a horizontal support under the pipe when I discovered that there is a second, identical crack around this pipe just a few inches from my repair!

It's like this pipe has some material defect to it, super brittle or something.

Again, the crack is perfectly around the pipe. I had flexed the pipe slightly and noticed a line of water droplets suddenly appear along a circumferential line.
Thinking that perhaps I won't even need a saw this time.

NHAero
05-30-2020, 08:10 PM
No, combined. But toilet drain is min. three inch.
In some buildings where gray water is used for irrigation they are kept separate from black water
my understanding is that gray water and true sewage must be routed separately...is that not the case?

robt57
05-30-2020, 08:20 PM
my understanding is that gray water and true sewage must be routed separately...is that not the case?

I think is more about proximity to the vent having to be closer for toilet VS sinks etc.

unterhausen
05-30-2020, 08:49 PM
Apparently there was a stretch of time where some manufacturers made pipe with this sort of problem. We have a lot of ABS in our house, hopefully we dont' get much of this kind of thing. Can't get it around here, in Virginia the big box stores all carried it.

Dino SuegiĆ¹
05-30-2020, 09:23 PM
my understanding is that gray water and true sewage must be routed separately...is that not the case?

Graywater and blackwater are typically drained separately within the structure, because of the different contamination levels of the waters but also because of the larger 3" to 4" size of blackwater drains, until the graywater and blackwater reach the common (if graywater will not be recycled on-site, with rainwater, for irrigation, etc.) line out to sewer main.

Blackwater is all the used whitewater that contains human or pet excrement (ie toilet water).
Blackwater must be routed to on- or off-site sewage/sewer/septic only.

Graywater is all the rest of the used whitewater (contaminated by soap, etc, but not by human waste).
Graywater may be routed to sewage treatment, along with the blackwater, or it may be routed for re-use for irrigation, etc., once treated in an on-site graywater treatment tank.

https://www.nap.edu/openbook/21866/xhtml/images/p109.jpg

dddd
05-30-2020, 09:36 PM
Now I've found a full four cracks in this pipe, three that I can see and one that lets water drip down through the door frame a foot away from the repair but on the other side of it.:eek:

Any flexing of the pipe reveals these cracks along the lower 180 degrees of the pipe's diameter, as tiny beads of water make a line halfway around the pipe.

This pipe is 25 years old and is obviously not aging well. I can only hope that this issue doesn't occur in the other drain pipes in this house.

I am going to have to route this sink's drain pipe through the vanity, and tee it into the other sink's drain. It's either that, ...or run some kind of flex pipe, ...or more demo work to actually replace the faulty pipe with a rigid length of new ABS.

I'm fortunate that there are two sinks in this the upstairs master bedroom. So for now, I can just use the other sink.